Section 3002.1 requires elevator hoistways to be constructed in accordance with Section 707.
Section 707.2 requires openings through floor/ceiling and roof/ceiling to be protected by a shaft enclosure complying with this section.
Exception #7 states that in other than Goup I-2 and I-3 shaft enclosures are NOT required for a floor opening or an air transfer openings
that comply with:
7.1. Does not connect more than two stories.
7.2. Is not part of the required means of egress system, except as permitted in Section 1020.1.
7.3. Is not concealed within the building construction.
7.4. Is not open to a corridor in Group I and R occupancies.
7.5. Is not open to a corridor on nonsprinklered floors in any occupancy.
7.6. Is separated from floor openings and air transfer openings serving other floors by construction conforming to required shaft enclosures.
7.7. Is limited to the same smoke compartment.
In my instance I have an elevator in a two story building with B-occupancy.
The elevator is housed within for walls.
I consider that in this instance the elevator complies with exceptions 7.1 through to 7.7 and therefore the enclosure does not need to be fire rated.
Section 3006.4 requires that machine rooms require fire barriers having fire resistance rating not less than the required elevator hoistway rating.
I consider that the machine room is not required to be fire rated because the hoistway does is not required to be fire rated.
Section 707.12 requires the top of a shaft to be enclosed with a rated lid or terminate at the underside of the building roof deck.
If my elevator hoistway penetrates the main roof and extends above the main building roof, I believe both the above two requirements are not applicable.
Any expert comments are welcome.
(obviously the plan reviewer does not agree with this and requires a 1 hour rated shaft and machine room with a 1 hour rated lid)
Section 707.2 requires openings through floor/ceiling and roof/ceiling to be protected by a shaft enclosure complying with this section.
Exception #7 states that in other than Goup I-2 and I-3 shaft enclosures are NOT required for a floor opening or an air transfer openings
that comply with:
7.1. Does not connect more than two stories.
7.2. Is not part of the required means of egress system, except as permitted in Section 1020.1.
7.3. Is not concealed within the building construction.
7.4. Is not open to a corridor in Group I and R occupancies.
7.5. Is not open to a corridor on nonsprinklered floors in any occupancy.
7.6. Is separated from floor openings and air transfer openings serving other floors by construction conforming to required shaft enclosures.
7.7. Is limited to the same smoke compartment.
In my instance I have an elevator in a two story building with B-occupancy.
The elevator is housed within for walls.
I consider that in this instance the elevator complies with exceptions 7.1 through to 7.7 and therefore the enclosure does not need to be fire rated.
Section 3006.4 requires that machine rooms require fire barriers having fire resistance rating not less than the required elevator hoistway rating.
I consider that the machine room is not required to be fire rated because the hoistway does is not required to be fire rated.
Section 707.12 requires the top of a shaft to be enclosed with a rated lid or terminate at the underside of the building roof deck.
If my elevator hoistway penetrates the main roof and extends above the main building roof, I believe both the above two requirements are not applicable.
Any expert comments are welcome.
(obviously the plan reviewer does not agree with this and requires a 1 hour rated shaft and machine room with a 1 hour rated lid)