• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Fire Riser Location within New Room

glzath

Registered User
Joined
Apr 10, 2013
Messages
44
Location
Wadsworth, Ohio
Figured while I'm waiting to hear back from the AHJ, I'd post the question here, too.

IBC 2009 basis.

As part of an industrial addition/alteration project the client has asked for a new 3,200 SF S-1 storage room to be added. The location of the room would end up enclosing three existing fire risers at the back (outside wall) of the new room. As it stands now, you can enter the building, immediately turn right and go 30 feet along the exterior wall to get to the risers which are out in the open; not in a riser room. With the new storage room there would be a tripling of the distance to get to the risers with no clear path.

1. Can the risers be located in the back of the new room, open to that space or will they need their own secondary riser room?

or

2. Will the new storage room need to be designed so as to not enclose the risers and leave their access as it currently stands?

Thanks in advance,

Gary
 
Code is silent

Up to ahj requirements or wants

NOW, with that said you are not setting the new addition on top of any underground fire sprinkler pipe,, are you??

Also will the fire department connection stay in the same place??
 
Last edited by a moderator:
Existing risers to remain as is and are on the East exterior wall. New addition going on South wall 120' away. Will verify, though.

Thanks for the insight.
 
+ + + +

glzath,

See Section 509, in the `09 IFC, for identification of your fire equipment locations

[ i.e. - approved signage ].

Also, ...are there plans to install an entrance door directly to the Fire Riser Room

from the exterior rather than navigating on the interior ?

+ + + +
 
Top