Life_learner
REGISTERED
Apologies in advance, I cannot find more info in the IBC commentary.
Has anyone run into this before, with exterior walls adjacent to property lines?
I typically use the IBC Commentary to help figure out these items in the code, but I cannot find any commentary answering this item.
A bunch of staff members have already argued this question back and forth, any help will be greatly appreciated.
A-3 Assembly, a health club workout center, 2,000 sf, Type 5B Construction (CMU walls, wood joist/deck)
The west wall is only 3” from the property line, shown in black with labels.
Reading IBC table 706.4 party walls requires 3-hr, but footnote “a” reduces to 2-hr.
But the north and south walls are within 10’ from the property line, are they required to be 1-hr as per Table 602?
OR is it because the west wall abuts at 90 degrees then the north/south wall is protected by the 2-hr west wall?
Same question about the amount of window/door openings allowed in table 705.8, there are overhead coiling doors within 10’ from property line, do these openings need to be protected or does the west 2-hr protect these openings.
link below- plan shows layout.
Is there somewhere I could read more about these requirements?
ANY help is appreciated, -- thank you for your time.
projman.caldwell-assoc.com/_fle/FLDR-479-395653/CODE Questions Fire Separation.jpg
Has anyone run into this before, with exterior walls adjacent to property lines?
I typically use the IBC Commentary to help figure out these items in the code, but I cannot find any commentary answering this item.
A bunch of staff members have already argued this question back and forth, any help will be greatly appreciated.
A-3 Assembly, a health club workout center, 2,000 sf, Type 5B Construction (CMU walls, wood joist/deck)
The west wall is only 3” from the property line, shown in black with labels.
Reading IBC table 706.4 party walls requires 3-hr, but footnote “a” reduces to 2-hr.
But the north and south walls are within 10’ from the property line, are they required to be 1-hr as per Table 602?
OR is it because the west wall abuts at 90 degrees then the north/south wall is protected by the 2-hr west wall?
Same question about the amount of window/door openings allowed in table 705.8, there are overhead coiling doors within 10’ from property line, do these openings need to be protected or does the west 2-hr protect these openings.
link below- plan shows layout.
Is there somewhere I could read more about these requirements?
ANY help is appreciated, -- thank you for your time.
projman.caldwell-assoc.com/_fle/FLDR-479-395653/CODE Questions Fire Separation.jpg