Plans Approver
Silver Member
Re: Fire Seperation M/S1/M
With nonseparated mixed uses, once you hit the threshold of 12,000 sf in a fire area, you require sprinklers by applying the most restrictive applicable provision of Chapter 9 (508.3.2.1). So I think that 2009 707.3.9 clears up the separated mixed occupancy problem.
But, throughout this discussion, I was reading instead of thinking. While reading your post, I had a duh! moment. :idea: Place the fire separation 1 inch (more or less) into the M area and make the separation according to 2006 Table 706.3.9. The single occupancy M is separated according to code. So that the result is one fire area as M and another that is mixed occupancy of a very small M plus the S-1.
I feel better.
Kinda.Glennman CBO said:Is this the point you are making Plans Examiner?
With nonseparated mixed uses, once you hit the threshold of 12,000 sf in a fire area, you require sprinklers by applying the most restrictive applicable provision of Chapter 9 (508.3.2.1). So I think that 2009 707.3.9 clears up the separated mixed occupancy problem.
But, throughout this discussion, I was reading instead of thinking. While reading your post, I had a duh! moment. :idea: Place the fire separation 1 inch (more or less) into the M area and make the separation according to 2006 Table 706.3.9. The single occupancy M is separated according to code. So that the result is one fire area as M and another that is mixed occupancy of a very small M plus the S-1.
I feel better.