Hello Everyone - first time poster here. I am a mechanical engineer from Baton Rouge, LA (Geaux Tigers!).
I have recently been reviewing the ventilation requirements for a fire station's apparatus bay. The bay is to be used for storing the vehicles only, i.e. no repair, fueling, etc. I have reviewed the following adopted code versions in my state: NPFA 101-2015, NFPA 88A-2015, IBC-2015, and IMC-2015. The AHJ in my state has also issued an interpretation that extends the Private Garage applicability to up to 3,000 square feet in lieu of the 1,000 square feet stated in the IBC. I have two separate sites I am designing with one of the apparatus bays being 2,000 square feet and the other is 5,000 square feet. Currently, the smaller bay is classified as a Group U occupancy and is being considered a Private Garage. The larger is Group S-2 and is being considered an Enclosed Parking Garage.
The conclusion I get from all of these codes is that some form of continuous ventilation is required in the apparatus bay. Below is what I have found in each code that states a ventilation rate.
NPFA 88A, 6.3.1: All enclosed parking structures shall be ventilated by a mechanical system capable of providing a minimum of 1 CFM/sq. ft. during hours of normal operation.
IMC 2015, Table 403.3.1.1 for Private and Public Garages - 0.75 CFM/sq. ft.
IMC 2015, Section 404 for Public Enclosed Parking Garages - You can provide CO and NO2 monitoring to reduce the rate to 0.05 CFM/sq.ft during times that the CO and NO2 levels are "normal". If CO or NO2 alarm trips, the rate increases to 0.75 CFM/sq. ft.
I have discussed this with many colleagues and have received a mixed bag of answers. Some have not ventilated at all, some provide the CO/NO2 monitors with no constant exhaust, some provide "comfort" ventilation fans with manual control....
My thought is that if I have to compare the NFPA 88A to the IMC 2015 and take the most stringent, I'll be ventilating at 1 CFM/sq. ft. year round.
Any of your help and experience will be greatly appreciated!
I have recently been reviewing the ventilation requirements for a fire station's apparatus bay. The bay is to be used for storing the vehicles only, i.e. no repair, fueling, etc. I have reviewed the following adopted code versions in my state: NPFA 101-2015, NFPA 88A-2015, IBC-2015, and IMC-2015. The AHJ in my state has also issued an interpretation that extends the Private Garage applicability to up to 3,000 square feet in lieu of the 1,000 square feet stated in the IBC. I have two separate sites I am designing with one of the apparatus bays being 2,000 square feet and the other is 5,000 square feet. Currently, the smaller bay is classified as a Group U occupancy and is being considered a Private Garage. The larger is Group S-2 and is being considered an Enclosed Parking Garage.
The conclusion I get from all of these codes is that some form of continuous ventilation is required in the apparatus bay. Below is what I have found in each code that states a ventilation rate.
NPFA 88A, 6.3.1: All enclosed parking structures shall be ventilated by a mechanical system capable of providing a minimum of 1 CFM/sq. ft. during hours of normal operation.
IMC 2015, Table 403.3.1.1 for Private and Public Garages - 0.75 CFM/sq. ft.
IMC 2015, Section 404 for Public Enclosed Parking Garages - You can provide CO and NO2 monitoring to reduce the rate to 0.05 CFM/sq.ft during times that the CO and NO2 levels are "normal". If CO or NO2 alarm trips, the rate increases to 0.75 CFM/sq. ft.
I have discussed this with many colleagues and have received a mixed bag of answers. Some have not ventilated at all, some provide the CO/NO2 monitors with no constant exhaust, some provide "comfort" ventilation fans with manual control....
My thought is that if I have to compare the NFPA 88A to the IMC 2015 and take the most stringent, I'll be ventilating at 1 CFM/sq. ft. year round.
Any of your help and experience will be greatly appreciated!