Big Mac,
Which code sections require the " 13 " vs a " 13R "?
.
Which code sections require the " 13 " vs a " 13R "?
.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Same one which doesn't require a hood over the fire station's cooktop.globe trekker said:Big Mac, Which code sections require the " 13 " vs a " 13R "?
That includes disabled firefightersTheCommish said:So a citizen will never come to the station to get a report, be interviewed in connection with an incident, the town fathers, mayor, congressman will never visit the station, he will never hire a administrative assistant, have his mother visit or have a fire prevention week open house with the public visiting the station. All or any that any that may need accessibility accommodations, remember it is not just wheelchair bound people, people with walkers, canes, people with problems grasping, things in their hands.
Even able body persons enjoy the conveyance of accessibility accommodations.
I think the OP said only able bodied would be permitted in the building...I guess those you mentioned would have to sit outside until they get better. j/kmtlogcabin said:From the OP it is the shower the FC states will not be used by the public. I guess there has never been a fire fighter come back from a call with a twisted knee, sprained ankle or strained back or maybe just overly exhausted that may need or want a rail to hang onto so the don't slip or fall while getting cleaned up before seeking treatment
Office Area (B)Big Mac said:13R systems are for Residential Strucutures, hence the 'R'. It was not intneded for use in Commercial strucutres dedicated primarily to ohter uses such as 'S' / 'A' / 'B' which are the uses normally found in Fire Stations. If that were not he case, why would even have a standard other than NFPA13?
As you and many others on this board have helped me to recognize, there are limits to my knowledge, and in some cases it is best to seek guidance from the access-board and/or DOJ. That being said, I do not enforce the ADA, but rather the accessibility standards my jurisdiction has adopted. I have not been told this, however, I assume, yet make no certain claim, that we have adopted certain codes and standards to help ensure that those facilities within our jurisdiction will also be compliant with the ADA and avoid a lawsuit. Furthermore, the fire stations that fall within our jurisdiction receive no exemption from Chapter 11 IBC compliance for accessibility.mark handler said:I say contact the DOJ. Seeing some of the comments from many on this board, makes me question their Knowledge
Here is 20 pages of SETTLEMENT AGREEMENTs between cities and the DOJ regarding access to Fire stations
http://searchjustice.usdoj.gov/search?q=%22fire+station%22&btnG=Search+ADA+Website&q=site%3Awww.ada.gov&sort=date%3AD%3AL%3Ad1&output=xml_no_dtd&ie=iso-8859-1&oe=UTF-8&client=default_frontend&proxystylesheet=default_frontend&site=default_collection&ip=71.189.92.234%2C10.4.254.29%2C10.14.4.33&access=p&entqr=0&entqrm=0&ud=1&start=0
Because sometimes the commercial uses of a building or structure require or benefit from a higher level of protection - 13R protects occupants who may be sleeping. 13 also protects structures, occupants who may be restrained, can be used in lieu of one hour fire protection, allows for additional square footage with a given construction type, etc. In a fire station, the purpose of the sprinkler system is to allow sleeping occupants time to escape.Big Mac said:13R systems are for Residential Strucutures, hence the 'R'. It was not intneded for use in Commercial strucutres dedicated primarily to ohter uses such as 'S' / 'A' / 'B' which are the uses normally found in Fire Stations. If that were not he case, why would even have a standard other than NFPA13?
Presumably the chief fires disabled personnel.mtlogcabin said:From the OP it is the shower the FC states will not be used by the public. I guess there has never been a fire fighter come back from a call with a twisted knee, sprained ankle or strained back or maybe just overly exhausted that may need or want a rail to hang onto so the don't slip or fall while getting cleaned up before seeking treatment
Contact the Access Board or DOJglobe trekker said:I have to claim lack of knowledge on all of this!
With handicapp bathroom in quarters (with shower) and in offices and front lobby (Yes 3)hlfireinspector said:Just finshed building new station:Bay S-1
Offices B
Living quarters R-2
Fully sprinklered NFPA 13
Our fire house was used for first aid classes, and Hunter's Ed classes. We had people stopping by for social visits. Girl Scouts stopped to sell cookies. Our kids stopped by so the girls could show us how pretty they were before the Prom. We also took the opportunity to glare at the boyfriend. We lived in the station for 24 hours at a time, it was our home away from home.globe trekker said:I have to claim lack of knowledge on all of this! I was hoping that some of the experiencedpersons from the Fire Community (on here) would chime in to assist in the discussion.
In looking at the descriptions for the different Occupancy Groups (in the 2006 IBC), I
would interpret these fire stations to be an R-2. I am also curious as to what others
(specifically from the Fire Community) would interpret these fire stations as.