fire starts inside compacted trashfire transitions into building
building burns down
section covers inside and outside and requries different coverage depending on::
22.15.2.3 Waste Handling Systems.
22.15.2.3.1 Automatic sprinklers shall be installed in rooms where waste handling systems and equipment are used to transport waste from interim storage areas to waste processing equipment, such as incinerators. [82:6.4.1]
22.15.2.3.2 In locations or rooms where waste handling systems and equipment are used for interim storage of waste only, the rooms shall be sprinklered in accordance with requirements specified in 22.15.2.4. [82:6.4.2]
22.15.2.4 Waste Compactors. [82:7]
22.15.2.4.1 All chute-fed compactors shall have an automatic sprinkler with a minimum 13 mm (½ in.) orifice installed in the hopper of the compactor. [82:7.2.1]
22.15.2.4.2 Sprinklers shall be ordinary temperature-rated sprinklers. [82:7.2.1.1]
22.15.2.4.3 Sprinklers shall be supplied by a minimum of 1 in. (25.4 mm) ferrous piping or ¾ in. (19 mm) copper tubing line from the domestic cold water supply or by the building fire sprinkler system. [82:7.2.1.2]
22.15.2.4.4 Sprinkler water pipe shall be protected from freezing in outdoor installations. [82:7.2.1.3]
22.15.2.4.5 Hand-fed compactors located within a building and not operated in conjunction with a chute shall not require installation of an automatic sprinkler in the hopper. [82:7.2.2]
22.15.2.5 Waste and recyclables storage rooms shall be provided with automatic sprinklers. [82:8.3]
22.15.2.6 Rooms in which waste processing equipment is located shall be installed with automatic sprinklers. [82:9.4.1]