Fast_Edd1e
REGISTERED
I am working on a change of use building that defers alot of the requirements back to the IBC. (Michigan building code)
When it comes to I-4 for daycare facilitys, the code states. Section 903.2.6 for Group I exception 2. Sprinkler not required in Group I-4 where each care area is provided with one exterior exit door. Which this facility will have.
However, when it comes to corridor fire rating. The chart on 1020.1 says its Not Permitted without sprinkler system.
Does this chart take into effect the use of the exception 2 for fire suppression requirements? Since the corridor is not a required means of egress with the exit doors? Or does the corridor push it to be required?
Thanks
When it comes to I-4 for daycare facilitys, the code states. Section 903.2.6 for Group I exception 2. Sprinkler not required in Group I-4 where each care area is provided with one exterior exit door. Which this facility will have.
However, when it comes to corridor fire rating. The chart on 1020.1 says its Not Permitted without sprinkler system.
Does this chart take into effect the use of the exception 2 for fire suppression requirements? Since the corridor is not a required means of egress with the exit doors? Or does the corridor push it to be required?
Thanks