NFPA 13 8.15.7 Exterior Projections is pretty clear that fire suppression is not needed under a canopy of non-combustible materials and where there is no storage or parked vehicles in I-2 occupancy.
However, IBC 903.2.6 requires fire suppression throughout a building "Fire Area" which is defined in 202 as "The aggregate floor area enclosed and bounded by fire walls, fire barriers, exterior walls or horizontal
assemblies of a building. Areas of the building not provided with surrounding walls shall be included in the fire area if such areas are included within the horizontal projection of the roof or floor next above."
Is there a way to rectify this apparent contradiction to not require fire suppression in I (or other) occupancy under IBC?
I'm wondering if the key is 903.3.1.1 NFPA 13 Sprinkler Systems "shall be installed in accordance with NFPA 13" and therefor the canopy is exempted by NFPA 13.
However, IBC 903.2.6 requires fire suppression throughout a building "Fire Area" which is defined in 202 as "The aggregate floor area enclosed and bounded by fire walls, fire barriers, exterior walls or horizontal
assemblies of a building. Areas of the building not provided with surrounding walls shall be included in the fire area if such areas are included within the horizontal projection of the roof or floor next above."
Is there a way to rectify this apparent contradiction to not require fire suppression in I (or other) occupancy under IBC?
I'm wondering if the key is 903.3.1.1 NFPA 13 Sprinkler Systems "shall be installed in accordance with NFPA 13" and therefor the canopy is exempted by NFPA 13.