Greetings,
2012 IBC
Type IIB construction
H-3 classification
Client desires a 120 x 400 = 48,000 SF. Open yard is more than 60 feet. Per 506.3 a sprinkler system increase is not allowed due to the H-3. I assume that a front yard increase is still allowed as I am not reading anything different.
If one 3-hour fire wall splits the building into two 120 x 200 buildings, my allowable area depends on whether or not I can include the fire wall perimeter as frontage. My assumption is that I cannot.
Here's some fun math:
Frontage Increase (IBC 506.2)
Building 1 - Group H-3:
If = [F/P-0.25]W/30
If = [440/640-0.25]30/30
If = [0.438]1
If = 0.438
Building 2 - Group H-3:
If = [F/P-0.25]W/30
If = [440/640-0.25]30/30
If = [0.438]1
If = 0.438
Total Area Modification - Aa = {At + [At x If] + [At x Is]}
Building 1 - Group H-3:
Aa = {14,000 + [6,132] + [0]}
Aa = 20,132 SF
Building 2 - Group H-3:
Aa = {14,000 + [6,132] + [0]}
Aa = 20,132 SF
Proposed Floor Area
Building 1 - Group H-3: 24,000 SF > 20,132 SF
Building 2 - Group H-3: 24,000 SF > 20,132 SF
Therefore, there would need to be two fire walls separating the building into 3 separate buildings, correct?
2012 IBC
Type IIB construction
H-3 classification
Client desires a 120 x 400 = 48,000 SF. Open yard is more than 60 feet. Per 506.3 a sprinkler system increase is not allowed due to the H-3. I assume that a front yard increase is still allowed as I am not reading anything different.
If one 3-hour fire wall splits the building into two 120 x 200 buildings, my allowable area depends on whether or not I can include the fire wall perimeter as frontage. My assumption is that I cannot.
Here's some fun math:
Frontage Increase (IBC 506.2)
Building 1 - Group H-3:
If = [F/P-0.25]W/30
If = [440/640-0.25]30/30
If = [0.438]1
If = 0.438
Building 2 - Group H-3:
If = [F/P-0.25]W/30
If = [440/640-0.25]30/30
If = [0.438]1
If = 0.438
Total Area Modification - Aa = {At + [At x If] + [At x Is]}
Building 1 - Group H-3:
Aa = {14,000 + [6,132] + [0]}
Aa = 20,132 SF
Building 2 - Group H-3:
Aa = {14,000 + [6,132] + [0]}
Aa = 20,132 SF
Proposed Floor Area
Building 1 - Group H-3: 24,000 SF > 20,132 SF
Building 2 - Group H-3: 24,000 SF > 20,132 SF
Therefore, there would need to be two fire walls separating the building into 3 separate buildings, correct?