2015 IBC
Existing building with F-1, S-1, S-2, B use groups. Proposed addition with F-1 and S-2 use groups.
I need to separate a 40 ft tall proposed addition from a 27 ft tall existing building with fire rated construction. The speed humps I encounter are that the structural engineer wants the addition to be about 3 feet from the existing building to minimize roof strengthening requirements due to snow drift loads on the existing lower roof and the owner wishes to retain a courtyard to maintain existing refrigeration equipment.
Since the proposed 3 hour FIRE RATED wall is not immediately adjacent to all existing building walls,
1. Can this still be considered a 3 hour rated FIRE WALL to create separate buildings?
2. Are the existing Type 3B non-rated building walls in violation of Table 602 for not having a minimum 30 ft fire separation distance?
3. Can the unrated overhead door be placed in the unrated wall?
Thanks
Existing building with F-1, S-1, S-2, B use groups. Proposed addition with F-1 and S-2 use groups.
I need to separate a 40 ft tall proposed addition from a 27 ft tall existing building with fire rated construction. The speed humps I encounter are that the structural engineer wants the addition to be about 3 feet from the existing building to minimize roof strengthening requirements due to snow drift loads on the existing lower roof and the owner wishes to retain a courtyard to maintain existing refrigeration equipment.
Since the proposed 3 hour FIRE RATED wall is not immediately adjacent to all existing building walls,
1. Can this still be considered a 3 hour rated FIRE WALL to create separate buildings?
2. Are the existing Type 3B non-rated building walls in violation of Table 602 for not having a minimum 30 ft fire separation distance?
3. Can the unrated overhead door be placed in the unrated wall?
Thanks