Mr. Inspector
SAWHORSE
2009 IBC. A 5B building is going to get a 2 hour fire wall between R-3 and S-2 occupancys so they only need sprinklers on the R side of the building. The building is 1 story and is not big enough to need sprinklers but needs it because of the R.
There is a porch roof that continues from the R side of the fire wall to the S side. The designer is asking me if they can extend the fire wall inside the porch roof to comply. I told him that it will need to be suported by a 2 hour rated column.
Would this comply with IBC 706.5.2 Horizontal projecting elements?