ok from the land of 101::
since clean agents requier a fire alarm system to make it work, should apply, and also since there are no sprinklers in the area, looks like the sprinkler impairment would apply to the clean agent room
are you just looking into,"if they do hot work in a clean room"??? YOu just might want the system shut down if they do !!!
fire alarm::
9.6.1.6* Where a required fire alarm system is out of service for more than 4 hours in a 24-hour period, the authority having jurisdiction shall be notified, and the building shall be evacuated, or an approved fire watch shall be provided for all parties left unprotected by the shutdown until the fire alarm system has been returned to service.
A.9.6.1.6
A.9.6.1.6 A fire watch should at least involve some special action beyond normal staffing, such as assigning an additional security guard(s) to walk the areas affected. Such individuals should be specially trained in fire prevention and in occupant and fire department notification techniques, and they should understand the particular fire safety situation for public education purposes. (Also see NFPA 601, Standard for Security Services in Fire Loss Prevention .)
The term out of service in 9.6.1.6 is intended to imply that a significant portion of the fire alarm system is not in operation, such as an entire initiating device, signaling line, or notification appliance circuit. It is not the intent of the Code to require notification of the authority having jurisdiction, or evacuation of the portion of the building affected, for a single nonoperating device or appliance.
9.7.6 Sprinkler System Impairments. Sprinkler impairment procedures shall comply with NFPA 25, Standard for the Inspection, Testing, and Maintenance of Water-Based Fire Protection Systems.
from NFPA 1:::
13.1.7 All fire protection systems and devices shall be maintained in a reliable operating condition and shall be replaced or repaired where defective or recalled.
13.1.8 The AHJ shall be notified when any fire protection system is out of service and on restoration of service.
13.1.9 When a fire protection system is out of service for more than 4 hours in a 24-hour period, the AHJ shall be permitted to require the building to be evacuated or an approved fire watch to be provided for all portions left unprotected by the fire protection system shutdown until the fire protection system has been returned to service.
13.1.10 In the event of a failure of a fire protection system or an excessive number of accidental activations, the AHJ shall be permitted to require an approved fire watch until the system is repaired.