Fireblocking materials?
steveray
West of the river CT
FROM THE 2009 IRC...........7. Batts or blankets of mineral wool or glass fiber or other approved materials installed in such a manner as to be securely retained in place.
DOES THIS MEAN IF YOU INSULATE YOUR WALLS (fiberglass), THAT YOU DON'T HAVE TO SEAL ANY PENETRATIONS? Sorry not yelling, but our stupid MUNIS software only works in caps...... :)
CT had amended this section (to exclude fiberglass)in the IRC and left it in the IBC for some reason.....I don't know where they will go w/ the next adoption, but I am trying to get ahead of the curve....
No change to #7 in the 2012 IRC however..they added a # 8
8. Cellulose insulation installed as tested for the specific
application.
I did see that Mule.....I was wondering if I am interpreting that improperly....it seems as though you need no fireblocking for penetrations if the cavity is full of fiberglass.....Is that correct?
Yes, however if you look at the next section the code gives specifics for fiberglass batts as fireblocking.
R302.11.1.1 Batts or blankets of mineral or glass fiber. Batts
or blankets of mineral or glass fiber or other approved nonrigid
materials shall be permitted for compliance with the 10-foot
(3048 mm) horizontal fireblocking in walls constructed using
parallel rows of studs or staggered studs
Remember the most you can go without horizontal fireblocking is 10 ft. Fiberglass shall be permitted for compliance with the 10-foot horizontal fireblocking in walls . So if it's a full cavity...yes you may use the fiberglass for fireblocking!
There was a BO from another city and we were having a discussion on fireblocking/draftstopping. He pointed out a section of the code where it talked about fireblocking at eaves and overhangs and stated that no AHJ requires fireblocking in that void between the eave and the gap that it creates on the exterior wall. That's when this exact section come in! The fiberglass is an approved fireblock/draftstop.
mtlogcabin said:
So how would you fire block an ICF wall when using http://www.strongtie.com/products/connectors/ICFVL.asp to support the second floor?Or is it not a concern if the sheetrock is attached directly to the foam? Might be overthinking this as it relates to ICF construction.
Don't know! Haven't thought about it! I'm thinking and have figured out my brain is hurting...........I'll get back with you on this same date next year!
Fireblocking only is required for combustionable construction. The ICF may have been fire tested for flammability and flame spread. IF the insulation meets the requirements, it is providing the fireblocking...... You will need to check the manufacture's listing of the ICF to ensure it has been tested correctly.
(In other words, If the ICF form can meet the same flame spread, smoke development, and thermal protection as sheetrock..... what is the problem?)