Sorry if this is bone head question but it has been a while since I have to use a firewall to seperate buildings. I have a single level storage facility project. A metal building supplier is providing the all metal storage buildings. I am designing a wood frame building that one of the storage building abut into. The wood frame structure (1-story Type V-non-rated) is 1200 sqft office (B occupancy) and 2000 sq ft. of storage (S1 occupancy). The metal storage building (assumed Type II -S1 occupancy)will abut the S-1 occupancy of the wood frame building. I need to seperate the two structures, with a fire wall becuase the total sq ftg exceeds 9000 sq ft.. IBC Table 706.4 indicates that the firewall needs to have a 3-hr rating. There is no water to this site so sprinkling is not an option. I do not see any exceptions or footnotes that would change the 3-hr rating.
Agree so far?
The owner/contractor would prefer to frame the wall in wood studs. I ran into this problem about 8 years ago it does not seem much has changed. I can not find a rated 3-hr wood stud assembly in the UL listing nor GA-600 manual. I find metal studs & cmu assemblies. I find in a UL document BXUV.U419 a discussion how 3 layer of 1/2" or 5/8" gyp board ea. side will give you a 3-hr rating but no actual assembly is listed. Can anyone point me in the direction of a 3-HR wood stud assembly or am I barking up the wrong tree. Framing up a metal stud fire wall is a fall back or is there another solution I am missing. Thank folks in advance.
Agree so far?
The owner/contractor would prefer to frame the wall in wood studs. I ran into this problem about 8 years ago it does not seem much has changed. I can not find a rated 3-hr wood stud assembly in the UL listing nor GA-600 manual. I find metal studs & cmu assemblies. I find in a UL document BXUV.U419 a discussion how 3 layer of 1/2" or 5/8" gyp board ea. side will give you a 3-hr rating but no actual assembly is listed. Can anyone point me in the direction of a 3-HR wood stud assembly or am I barking up the wrong tree. Framing up a metal stud fire wall is a fall back or is there another solution I am missing. Thank folks in advance.