Thanks AegisPE, CDA, Insurance Engineer, PermitGuy!
Here are the answers to the questions. Is 30' the clearance or 5'? Is the tank considered protected because of the housing?
1. What is the computer bld. wall made of any fire rating, is it concrete block, metal or glass? Any windows/doors in the wall? How will the wall hold up should a fire occur at the generator? No walls, windows or doors it is made of concrete
2. Is the generator higher or lower then the data center? Will a pool fire involving the diesel fuel at the generator flow back to the building? Is the ground between the building and the generator soil, concrete, blacktop? The ground between is grass covered and the generator and tank are slightly below grade with respect to the computer room
3.Any fire suppression system in the generator enclosure? Nope
4. Any secondary containment around the generator to prevent the flow of fuel to the computer building?The generator came with an enclosure, the tank is double walled nothing additional
5. Have you asked your insurance carrier for advise?? They may be able to help you, since they get to pay the loss. Not yet
6. Does the computer building have a sprinkler system installed? yes the computer room is sprinklered