Flatscreen Televisions and Drop Ceilings
You walk into a conference room of a recent renovation for a final electrical inspection and see a new flatscreen TV mounted on the wall. You then see the power cord for the TV running up the wall and through the drop ceiling. Above the ceiling is a receptacle that the TV is plugged into.
Is that a legal installation per the NEC?
400.8 Uses Not Permitted.
Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following:
(1) As a substitute for the fixed wiring of a structure
(2) Where run through holes in walls, structural ceilings, suspended ceilings, dropped ceilings, or floors
(3) Where run through doorways, windows, or similar openings
(4) Where attached to building surfaces
Exception to (4): Flexible cord and cable shall be permitted to be attached to building surfaces in accordance with the provisions of 368.56(B)
(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
(6) Where installed in raceways, except as otherwise permitted in this Code See related ROP ROC
(7) Where subject to physical damage
Gregg Harris said:
Take a look at UL 817 and UL 62Chapter 4 does not cover power supply cords for equipment
I disagree, the scope of 400 covers flexible cords and cables. If a listed cord set is constructed of a flexible cord of the type listed in 400.4 then the installation of that cord set in a building falls under Article 400.
Chris
jar546 said:
I think the issue is to whether or not Chapter 4 covers power cords for appliances.....................Hmmmmmmm
422.16 applies to appliance power cords specifically waste disposers, dishwashers, trash compactors, range hoods, ranges and counter mounted cooking units.
Chris
Ceiling-mounted projectors almost always violate this. I hate to think how many times I've had to be a bad guy and tell the dean that they messed up on the newly remodeled classroom he's showing off.
Put the receptacle in the ceiling and they are good to go.....