Looks like you typed in the proper loading. I assume the results are correct. I don't like the format, but ...jar546 said:This is what the "engineers" gave to me. Comment?http://inspectpa.com/download/GirderSample1.pdf
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Looks like you typed in the proper loading. I assume the results are correct. I don't like the format, but ...jar546 said:This is what the "engineers" gave to me. Comment?http://inspectpa.com/download/GirderSample1.pdf
One nice part of being an engineer is that you can write up a spread sheet to "do it your way."DRP said:I am running the "pass/fail" on total load rather than LL only.... annoying floor vibration.
But . . . what?GHRoberts said:but ...
I looked at the second page expecting to see calcs for a 4-ply beam?dhengr said:Is there some mysterious difference btwn. pages 1 & 2 of your attachment?
Respectfully, why? The balance of prescriptive spans, combined with the other elements prescripted in the IRC are thought to be conservative enough not to worry about a full accounting of the loads on an individual girder. In other words, if the codebook formulas are derivative of conservative engineering, then it is not necessary to have a full accounting of the loads in order to use the tables. I always imagined that when engineers, architects, and other design professionals were designing framing elements for a home, something as basic as described in this thread, that even you guys turned to span charts here and again.dhengr said:I keep screaming for a full accounting of the loads on that girder.
Jobsaver said:It stands to reason that one can increase the span by about 25% if one adds one additional ply to a 2-ply 2x6 girder, and, for damn sure, if one adds two additional plys to a 2-ply 2x6 girder. In my example in the OP, I need to get from 4-6 (2-ply 2x6 girder) to 5-8, a 25.7% increase in span.
Jobsaver said:the builder, who says, "this historically works"
It seems to me that we are all saying the same thing. And, that every party is reaching the same conclusion: A 3-ply girder will probably work okay, but it is close, and depending on where the walls are . . . you might want to make it a 4-ply just to be sure.DRP said:The math can be shown to work at 3 ply but there's certainly nothing wrong with 4-ply, there is no need to pass by the skin of our teeth.
As a "PE" I do not work for the AHJ. I provide information to my clients. That information is never stamped. My clients have the option of passing the information on to the AHJ if they desire. (Unless I am doing the actual physical construction the engineering is for "informational" purposes only.)jar546 said:I would need a stamped spec sheet from a PE if they did not want to comply prescriptively. That is truly the bottom line.
George, you are really working hard to find something to be a detractor about, huh?GHRoberts said:As a "PE" I do not work for the AHJ. I provide information to my clients. That information is never stamped. My clients have the option of passing the information on to the AHJ if they desire. (Unless I am doing the actual physical construction the engineering is for "informational" purposes only.)I believe the code requires "engineering" not work by an engineer. Certainly not work containing an engineer's "stamp."
---
The nice part of engineering is that anyone can do it for themselves. Most people don't have a "stamp."
The "But" indicates it is not up to me to accept it or reject it.Jobsaver said:But . . . what?
You said you require an engineer's stamp. Show me the code section that requires an applicant to provide a stamp.jar546 said:George, you are really working hard to find something to be a detractor about, huh?BTW, I don't care who hires or pays the PE or who the PE is working for as it is the permit applicant who must submit it to the AHJ before work can continue or begin.
jar546 said:I still find myself calling up the experts to verify I am inputing the correct data.
Given a choice, should I be counting on someone, I'd put my confidence in the man that is not afraid to ask a question, and understands the meaning of a sentence.GHRoberts said:I am amazed that you admit you don't know how to enter data into Beam Check, but you accept the results you get from doing so.
Did you notice that in post #24 Jar had the span wrong, the tributary "width" wrong, and the dead load wrong?Jobsaver said:Given a choice, should I be counting on someone, I'd put my confidence in the man that is not afraid to ask a question, and understands the meaning of a sentence.
Jobsaver said:I see printed, Uniform LL:400, and, Uniform TL: 500 = A, but these fiqures do not mean anything to me as presented.
Thanks again DRP. I owe you an apple.DRP said:Jar did it right, lets work it longhand;10' trib width x #40LL= 400 plf LL
10' trib width x #10DL=100plf DL
LL+DL= 500PLF TL
class dismissed