By code (IBC/RBC) the truss manufacturer is REQUIRED to calc all Truss to Truss Connections. Truss to plate on the other hand is NOT required, not yet any way. Part of the rub is, if it's spelled out on the sealed drawings then that EXACT connection has to be used, eliminating your options. Therefore most truss suppliers provide that information separately on documents which have not been sealed. Invariably, if it's speced out on the seals it’s not what the contractor/home owner wanted to use for this particular job.
Calculating truss hardware is easy.
Roof Truss:
You have to use two bits of information found on the truss engineering drawings. Both should be found near the "Bearing" information block.
1- The Reaction
2- The uplift ( proceeded by a negative number)
Floor Truss:
Same procedure except you don't need the uplift values since there are no wind load calculations on a floor. Item “T”
Next Choose your hardware supplier:
Simpson Strong Tie ( ITW/Alpine they are not gonna buy from their competition)
USP (used with most MiTek engineered trusses, they own the company now)
The manuals are available on line and give you a graphic for the correct application, be careful here. You don’t want to choose hardware that is hanging in mid air with nothing in which to nail into.
For your Floor Truss with a single plate:
● Choose the correct application in the hardware catalog. (Attaching member, concrete or wood)
● Verify both the truss and the member being attached to is the correct application.
● Under the 160% (SPF) column choose a reaction/uplift that is equal or greater than the respective values on the truss engineering drawing.
● Check the chart for the correct size and qty of nails, being sure when you install, be sure to fill every hole.