Essentially, Florida does not have a Chapter 34 of the FBC Residential as it simply points to the 2020 NEC now that we are in the 8th Edition of the 2023 FBC. There was one entry in Chapter 34 worth mentioning.
Here is what the 2020 NEC says:
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.
Ground-fault circuit-interrupter protection for personnel shall be provided as required in 210.8(A) through (F). The ground-fault circuit interrupter shall be installed in a readily accessible location.
Informational Note No. 1:
See 215.9 for ground-fault circuit-interrupter protection for personnel on feeders.
Informational Note No. 2:
See 422.5(A) for GFCI requirements for appliances.
Informational Note No. 3:
See 555.9 for GFCI requirements for boat hoists.
Informational Note No. 4:
Additional GFCI requirements for specific circuits and equipment are contained in Chapters 4, 5, and 6.
For the purposes of this section, when determining the distance from receptacles the distance shall be measured as the shortest path the supply cord of an appliance connected to the receptacle would follow without piercing a floor, wall, ceiling, or fixed barrier, or the shortest path without passing through a window.
(F) Outdoor Outlets.
All outdoor outlets for dwellings, other than those covered in 210.8(A)(3), Exception to (3), that are supplied by single-phase branch circuits rated 150 volts to ground or less, 50 amperes or less, shall have ground-fault circuit-interrupter protection for personnel.
Exception No. 1:
Ground-fault circuit-interrupter protection shall not be required on lighting outlets other than those covered in 210.8(C).
Exception No. 2:
Ground-fault circuit-interrupter protection shall not be required for listed HVAC equipment. This exception shall expire September 1, 2026.
Here is what the FBC Residential says:
Here is what the 2020 NEC says:
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.
Ground-fault circuit-interrupter protection for personnel shall be provided as required in 210.8(A) through (F). The ground-fault circuit interrupter shall be installed in a readily accessible location.
Informational Note No. 1:
See 215.9 for ground-fault circuit-interrupter protection for personnel on feeders.
Informational Note No. 2:
See 422.5(A) for GFCI requirements for appliances.
Informational Note No. 3:
See 555.9 for GFCI requirements for boat hoists.
Informational Note No. 4:
Additional GFCI requirements for specific circuits and equipment are contained in Chapters 4, 5, and 6.
For the purposes of this section, when determining the distance from receptacles the distance shall be measured as the shortest path the supply cord of an appliance connected to the receptacle would follow without piercing a floor, wall, ceiling, or fixed barrier, or the shortest path without passing through a window.
(F) Outdoor Outlets.
All outdoor outlets for dwellings, other than those covered in 210.8(A)(3), Exception to (3), that are supplied by single-phase branch circuits rated 150 volts to ground or less, 50 amperes or less, shall have ground-fault circuit-interrupter protection for personnel.
Exception No. 1:
Ground-fault circuit-interrupter protection shall not be required on lighting outlets other than those covered in 210.8(C).
Exception No. 2:
Ground-fault circuit-interrupter protection shall not be required for listed HVAC equipment. This exception shall expire September 1, 2026.
Here is what the FBC Residential says:
E3408.1
NFPA 70-20: National Electric Code, Article 210 (Branch Circuits), Section 210.8, Ground-Fault Circuit-Interrupter Protection for Personnel, is amended to read as follows:- 210.8 Ground-Fault Circuit-Interrupter Protection for Personnel. Ground-fault circuit-interrupter protection for personnel shall be provided as required in 210.8(A) through (F). The ground-fault circuit-interrupter shall be installed in a readily accessible location.
- (F) Outdoor Outlets. All outdoor outlets for dwellings, other than those covered in 210.8(A)(3), Exception to (3) that are supplied by single-phase branch circuits rated 150 volts to ground or less, 50 amperes or less, shall have ground-fault circuit-interrupter protection for personnel.
- Exception No. 1: Ground-fault circuit-interrupter protection shall not be required on lighting outlets other than those covered in 210.8(C).
- Exception No. 2: GFCI protection shall not be required for listed and labeled HVAC equipment.
- Informational Note: See UL 60335-2-40, Household And Similar Electrical Appliances – Safety – Part 2-40: Particular Requirements for Electrical Heat Pumps, Air-Conditioners and Dehumidifiers or UL 1995, Heating and Cooling Equipment for product safety standards.(1)