bill1952
SAWHORSE
Just can't find in 2018 IRC but: where is requirement - seismic A, B, or C - for dowels or keyway between footing and stem wall? Certainly not shown in illustrations, Figure R403.1(1) for example, and not finding in text.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Maybe where you are from but around here they are seldom poured together. The footing is normally poured first and then the stem off poured separately with the forms for it set on top of the footing. This also allowed for the additional verticals required for the stem wall and the horizontals to be tied in place after the footing of poured.Typically the footing and the stem wall are poured together.
This is where I go. Footing in the IRC do require reinforcement.ACI 318 referenced from the IBC has provisions relevant to construction joints.
You've never poured a concrete wall. Pouring monolithically is 10x more difficult. Waterstops are much, much easier. Typically it's a bentonite waterstop at that location which is very easy to consolidate around and very effective. If the soil is well draining, they won't even use a waterstop and rely on the exterior waterproofing.So many problems created by two pours that would be solved if it was cast monolithically.
water stops create problems because it is difficult to consolidate the concrete near the water stop. This allows water to flow around the water stop.
When engineers want the equivalent of a monolithic joint the existing concrete is sandblasted and roughened. This allows the new concrete to bond to the existing. In addition reinforcing is cast in the first pour perpendicular to the joint to prevent slippage at the joint. If there is a concern about water leakage waterproofing is installed on the wet side.