jar546 said:
No go. Conditioned spaces must be properly insulated so registers in basements then require the basement to be insulated. You can't have it both ways to circumvent a code requirement
2012 IRC
N1101.4 (R101.4.5) Change in space conditioning.
Any nonconditioned space that is altered to become conditioned space shall be required to be brought into full compliance with this chapter.
CONDITIONED SPACE. For energy purposes, space within a building that is provided with heating and/or cooling equipment or systems capable of maintaining, through design or heat loss/gain,
50°F (10°C) during the heating season and 85°F (29°C) during the cooling season,
or communicates directly with a conditioned space. For mechanical purposes, an area, room or space being heated or cooled by any equipment or appliance.
If the basement already maintains a 50 degree f temp then nothing is required to be done to the basement walls or the duct system.
This is quite common in basements in my area of the country
MECHANICAL SYSTEM. A system specifically addressed and regulated in this code and composed of components, devices, appliances and equipment.
M1202.1 Additions, alterations or repairs.
Additions, alterations, renovations or repairs to a mechanical system shall conform to the requirements for a new mechanical system
without requiring the existing mechanical system to comply with all of the requirements of this code. Additions, alterations or repairs shall not cause an existing mechanical system to become unsafe, hazardous
or overloaded. Minor additions, alterations or repairs to existing mechanical systems shall meet the provisions for new construction, unless such work is done in the same manner and arrangement as was in the existing system, is not hazardous, and is approved.
The basement may already be conditioned by definition.
There are any number of things a homeowner does to their home that can positively or negatively effect the HVAC system. Have they installed new energy windows? Have they installed exterior insulation when residing the house? Did they add more blow in insulation in the attic? These are all questions the contractor needs to ask before determining the size of the HVAC unit. The additional heating load on the basement is minimal compared to the other issues. Is the original unit an old 80% and the new a 90% or 95% same size..
Remember this is not a new home and to do a designed system to the nats :butt size will not be possible. The contractor will have to err on the larger size of the calculated load range.