Francis Vineyard
REGISTERED
An engineer from the city’s natural gas supplier who contends that the electrical inspector has the authority enforce their clearance distance of the main disconnect from the outdoor gas meter regulator under article 500; class 1, division 1 hazard. Begin with the IRC scoping “Electrical systems, equipment or components not specifically covered in the chapter shall comply with the applicable provisions of the NFPA 70."
Your thoughts and has anyone heard of applying this to residential gas meters?
500.5 Classifications of Locations.
(A) Classifications of Locations. Locations shall be classified depending on the properties of the flammable gas, flammable liquid-produced vapor, combustible-liquid produced vapors, combustible dusts, or fibers/flyings that may be present, and the likelihood that a flammable or combustible concentration or quantity is present. Where pyrophoric materials are the only materials used or handled, these locations shall not be classified. Each room, section, or area shall be considered individually in determining its classification.
Informational Note: Through the exercise of ingenuity in the layout of electrical installations for hazardous (classified) locations, it is frequently possible to locate much of the equipment in a reduced level of classification or in an unclassified location and, thus, to reduce the amount of special equipment required.
Rooms and areas containing ammonia refrigeration systems that are equipped with adequate mechanical ventilation may be classified as “unclassified” locations.
The NEC does not classify specific Class I, II, and III locations. NFPA technical committees and the American Petroleum Institute (API), among other organizations with experience and expertise in working with flammable liquids, gases, vapors, dusts, fibers and flyings inherent to a process or present under abnormal conditions of operation, determine the parameters, distances, and degrees of hazard associated with classified locations. Some of this information has been extracted from other NFPA and API documents and is included in Articles 511through 517 of the Code.
In some facilities, an expert or team of experts, which may include a process engineer, a mechanical engineer, a safety engineer, and operations personnel, will use the information developed in those NFPA standards and apply it to their specific equipment and process and, depending on the materials and physical equipment and locations (for example, possible leaks at flanges, machinery seals), decide on the area classification, and produce the hazardous area diagram. See the commentary for 500.4(A). Common sense and good judgment must prevail in classifying an area that is likely to become hazardous and in determining those portions of the premises to be classified Division 1 or Division 2.
Francis
Your thoughts and has anyone heard of applying this to residential gas meters?
500.5 Classifications of Locations.
(A) Classifications of Locations. Locations shall be classified depending on the properties of the flammable gas, flammable liquid-produced vapor, combustible-liquid produced vapors, combustible dusts, or fibers/flyings that may be present, and the likelihood that a flammable or combustible concentration or quantity is present. Where pyrophoric materials are the only materials used or handled, these locations shall not be classified. Each room, section, or area shall be considered individually in determining its classification.
Informational Note: Through the exercise of ingenuity in the layout of electrical installations for hazardous (classified) locations, it is frequently possible to locate much of the equipment in a reduced level of classification or in an unclassified location and, thus, to reduce the amount of special equipment required.
Rooms and areas containing ammonia refrigeration systems that are equipped with adequate mechanical ventilation may be classified as “unclassified” locations.
The NEC does not classify specific Class I, II, and III locations. NFPA technical committees and the American Petroleum Institute (API), among other organizations with experience and expertise in working with flammable liquids, gases, vapors, dusts, fibers and flyings inherent to a process or present under abnormal conditions of operation, determine the parameters, distances, and degrees of hazard associated with classified locations. Some of this information has been extracted from other NFPA and API documents and is included in Articles 511through 517 of the Code.
In some facilities, an expert or team of experts, which may include a process engineer, a mechanical engineer, a safety engineer, and operations personnel, will use the information developed in those NFPA standards and apply it to their specific equipment and process and, depending on the materials and physical equipment and locations (for example, possible leaks at flanges, machinery seals), decide on the area classification, and produce the hazardous area diagram. See the commentary for 500.4(A). Common sense and good judgment must prevail in classifying an area that is likely to become hazardous and in determining those portions of the premises to be classified Division 1 or Division 2.
Francis