NEC 517.30 talks about Other Loads not discussed shall be served by their own transfer switches. 700.5 says transfer devices shall only be used for emergency loads.
517.30 seems to imply that nonessential (other) loads can be served by the generator as long as they are on a load shedding separated transfer switch that is designed to not overload the generator.
Is this a correct interpretation?