Power trip. I have a project in for permit review, a bank branch, about 3,600 sf. It’s in Maryland, construction type vb, occupancy B business. IBC 2018. After many weeks of nothing, the reviewer has come back with a laundry list of comments, a couple of which are a bit much to accept. The word from the AoR is that this reviewer has a really terrible reputation, and if you push back he finds even more issues. Here’s three that are bothersome.
We have an awning over the exterior atm and called out Sunbrella fabric. His comment is that the fabric has to flame spread rating (no problem there) and we have to provide proof that it is rated. Manufacturers spec sheets are not an acceptable form of documentation. Provide trst data from a NRTL.
Second item is occupancy load calculation. He wants to use 15 sf per person for conference room, break room, lunch room and other assembly areas, and 100 sf for the rest of the branch. That’s going to probably change the total occupancy and change the restroom requirements.
We provide small lockers in the breakroom for employees to secure thier purses and such. He says that’s a dressing/fitting/locker room and we need to provide a bench. No room for a bench, and no need.
We have an awning over the exterior atm and called out Sunbrella fabric. His comment is that the fabric has to flame spread rating (no problem there) and we have to provide proof that it is rated. Manufacturers spec sheets are not an acceptable form of documentation. Provide trst data from a NRTL.
Second item is occupancy load calculation. He wants to use 15 sf per person for conference room, break room, lunch room and other assembly areas, and 100 sf for the rest of the branch. That’s going to probably change the total occupancy and change the restroom requirements.
We provide small lockers in the breakroom for employees to secure thier purses and such. He says that’s a dressing/fitting/locker room and we need to provide a bench. No room for a bench, and no need.