grounding bars in main panels

turboterris

Member
Joined
Nov 15, 2014
Messages
1
Location
6038 w 38th AVE Kennewick wa 99338
I am a IBC, IRC, IFC code inspector. I am also a licensed electrician in AZ expired in 1990. I work in Pasco WA> therefore we do not inspect electrical installs. the State L&I dept does it throughout the state. I do a
Fire Safety Inspection of a High risk and Moderate risk businesses in the ciry. There is a question regarding having 2 grounding buss bars in main panels. When I was doing for hire building inspection [20 trs] we only required two bars in a subpanel. the neutral will become hot if the copper ground wire is not separated from the white neutral. I do not have an NEC book newer than 1989. I could look it up but shoot I have you guys out there that know chapter and verse.
 
I'm confused by your question. Are you asking about bonding of the neutral to the equipment grounding conductor in a main panel, that is, at the first means of disconnect?
 
Correct, anything downstream of the main panel will have grounds and neutrals separated...If that is what you are asking. If the panel came with a bonding jumper bar tieing them together it would have to be removed to be used as a subpanel. 250.122 maybe...Not an electrical guy...
 