Does anyone know of a specific NEC reg that says the backboard of a panel is not sufficient enough to maintain the integrity of a grounding circuit.
The circuit is 1000A through a disconnect. The ground conductors in are 3 each 4/0 cables and the very same out. However between in and out sets of cables the only continuation is through the panel itself.
There must be a regulation to say this is not sufficient.
 
If you mean the equipment grounding conductor the metal enclosure is fine.
If you mean the grounded conductor (neutral) then no. NEC 200.2(B)

Welcome to the forum.
 
If you mean the equipment grounding conductor the metal enclosure is fine.
If you mean the grounded conductor (neutral) then no. NEC 200.2(B)

Welcome to the forum.
Does anyone know of a specific NEC reg that says the backboard of a panel is not sufficient enough to maintain the integrity of a grounding circuit.
The circuit is 1000A through a disconnect. The ground conductors in are 3 each 4/0 cables and the very same out. However between in and out sets of cables the only continuation is through the panel itself.
There must be a regulation to say this is not sufficient.
GetAttachmentThumbnail
 
the above situation is whats in question. i just cant see how the integrity of the incoming grounding cables is transferred to the outgoing.
 
the above situation is whats in question. i just cant see how the integrity of the incoming grounding cables is transferred to the outgoing.


Your picture does not show unless you are a paid supporter of the fantastic site.