Grounding to rebar in footer vs ground ro
bnymbill
Baltimore
Can anyone identify when the IRC adopted the method of grounding to rebar in footers instead of a ground rod? My understanding is that it is required now but not sure when that officially changed in the IRC.
It is not "required" now. It is allowed, it's one of several options. The provisions allowing it date all the way back to the original 2000 IRC.
Your jurisdiction may have amended the model IRC. I researched it back through every edition of the ICC IRC from 2021 back to 2000.
Not familiar with the IRC's electrical chapters, but for the NEC, if the project scope includes installing a new concrete footing in direct contact with the earth, and the footing has 20' or more of #4 or larger rebar, then it is required to utilize at least one such footing as a Concrete Encased Electrode.
Cheers, Wayne
I believe E3608.1.2, Concrete-encased electrode specifies the requirement under 3608.1, Grounding electrode system. I was having trouble tying the different sections together but pretty sure that’s it.
I phrased my response poorly, but the requirement goes all the way back to the 2000 IRC. The language changed between (IIRC) 2003 and 2006, but the requirement didn't change.
Good deal and thanks for the replies/help!
I have a new construction home being built and they put the ground rod that was bonded to the footer in front of the egress window. They had to grind that rod off at the slab. Now, they have to put a new ground rod in but no way to bond it to the footer at this point.
I guess it’s also possible that the first ground rod wasn’t bonded to the footer because they wouldn’t need a rod at that point, the rebar electrode would take care of the code requirement by itself.
With the increased use of plastic water lines and the POCO's wanting their meter sockets grounded there has been a recent shift to a *Ufer type grounding system. I have seen foundation crews place TWO vertical rebar rods that stick up beyond the top of the poured foundation wall that are tied to the footings horizontal rebars at both ends of the foundation due to foundation crews not know the location of the houses main panel. They will spray paint theses rods orange, red or white to indicate they are to be used as a grounding source.
On the dufus side, I have seen the (GEC) coiled up on the inside of the foundation and later covered up by the concrete floor guy, said he didn't know what it was for?
FYI, for the ones that are non-experts.
After being asked in the field "What does Ufer mean?" I could tell them the purpose however after researching I found that Ufer is the name of the engineer Herbert G. Ufer, who developed the (CEE) concrete encased grounding electrode.
I had a smart-guy friend that knew a bit about grounding communication towers and he said "I don't want a house with that system!" and the curious George I' am, said why?
He explained "that if the house takes a lighting hit it could blow out the concrete wall!" and then you're left with a busted foundation issue!" I would think he'd have other issues as well.
I would like to know if anyone has seen the results of a lighting strike on a wall ufer set-up or would agree with that opinion?
I haven't seen a house with that grounding system that was struck by lightning, but I had the same concern when I first encountered the concept. A lightning strike will more than likely blow out the concrete around the rebar that's acting as the grounding conductor. I think it's a valid concern.
Maybe so, but if the alternative is for that energy to be dumped into the rest of the electrical system, better to repair some concrete than extensively repair the electrical system.
Cheers, Wayne
they will spray paint theses rods orange, red or white to indicate they are to be used as a grounding source.
A little paint:IMG_0013.JPG
Or a lot of paint:
Never a good idea.
The Ufer requirement came into the NEC code in 1978, but many jurisdictions tried to see a loophole in the language and did not require it. In the 2005 NEC, the language was clarified to make sure it would be enforced as originally intended. The IRC is a summarized version of the NEC for IRC houses, and is identical in purpose and intent to the NEC. The IRC electrical section is intended to be a direct copy of the NEC, just reworded a little.
If the footing has rebar in it and you had the opportunity to bond it and use the Ufer, around here we would make you either break concrete to find the Ufer or pour a new one in the yard.
If the house has a direct lightning strike, it won't matter either way - I think the house will have severe damage regardless. If it's "just" induced voltage from lightning, I doubt there will be any noticeable issues. I have never heard of any, but of course, I have never tested it.
Yeah, with a direct lightning strike I think your foundation would be the least of your troubles.
Out of curiosity I did a google image search for "lightning strikes concrete" and got some interesting results...