Not familiar with the IRC's electrical chapters, but for the NEC, if the project scope includes installing a new concrete footing in direct contact with the earth, and the footing has 20' or more of #4 or larger rebar, then it is required to utilize at least one such footing as a Concrete Encased Electrode.It is not "required" now. It is allowed, it's one of several options.
It is required if present. New construction, absolutely, renovation, not necessarily if the rebar is not accessible.It is not "required" now. It is allowed, it's one of several options. The provisions allowing it date all the way back to the original 2000 IRC.
I had a smart-guy friend that knew a bit about grounding communication towers and he said "I don't want a house with that system!" and the curious George I' am, said why?
He explained "that if the house takes a lighting hit it could blow out the concrete wall!" and then you're left with a busted foundation issue!" I would think he'd have other issues as well.
I would like to know if anyone has seen the results of a lighting strike on a wall ufer set-up or would agree with that opinion?
Maybe so, but if the alternative is for that energy to be dumped into the rest of the electrical system, better to repair some concrete than extensively repair the electrical system.I haven't seen a house with that grounding system that was struck by lightning, but I had the same concern when I first encountered the concept. A lightning strike will more than likely blow out the concrete around the rebar that's acting as the grounding conductor. I think it's a valid concern.