Group U structure - firewall question, IBC 2009
Also, does anyone know if there is a fire rating for metal? I though perhaps putting that heaving gauge "Rusty Metal" roofing material on the end for the fire wall??
705.11 Parapets.
Parapets shall be provided on exterior walls of buildings.
Exceptions: A parapet need not be provided on an exterior wall where any of the following conditions exist:
1. The wall is not required to be fire-resistance rated in accordance with Table 602 because of fire separation distance .
2. The building has an area of not more than 1,000 square feet (93 m2) on any floor.
3. Walls that terminate at roofs of not less than 2-hour fire-resistance-rated construction or where the roof, including the deck or slab and supporting construction, is constructed entirely of noncombustible materials.
4. One-hour fire-resistance-rated exterior walls that terminate at the underside of the roof sheathing, deck or slab, provided:
4.1. Where the roof/ceiling framing elements are parallel to the walls, such framing and elements supporting such framing shall not be of less than 1-hour fire-resistance-rated construction for a width of 4 feet (1220 mm) for Groups R and U and 10 feet (3048 mm) for other occupancies, measured from the interior side of the wall.
4.2. Where roof/ceiling framing elements are not parallel to the wall, the entire span of such framing and elements supporting such framing shall not be of less than 1-hour fire-resistance-rated construction.
4.3. Openings in the roof shall not be located within 5 feet (1524 mm) of the 1-hour fire-resistance-rated exterior wall for Groups R and U and 10 feet (3048 mm) for other occupancies, measured from the interior side of the wall.
4.4. The entire building shall be provided with not less than a Class B roof covering.