Are you required to group disconnects for townhouses?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
230.71 Maximum Number of Disconnects.(A) General. The service disconnecting means for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception No. 1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers, or a combination of not more than six switches and sets of circuit breakers, mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard. There shall be not more than six sets of disconnects per service grouped in any one location.
For the purpose of this section, disconnecting means installed as part of listed equipment and used solely for the following shall not be considered a service disconnecting means:
(1) Power monitoring equipment
(2) Surge-protective device(s)
(3) Control circuit of the ground-fault protection system
(4) Power-operable service disconnecting means
(B) Single-Pole Units. Two or three single-pole switches or breakers, capable of individual operation, shall be permitted on multiwire circuits, one pole for each ungrounded conductor, as one multipole disconnect, provided they are equipped with identified handle ties or a master handle to disconnect all conductors of the service with no more than six operations of the hand.
FPN: See 408.36, Exception No. 1 and Exception No. 3, for service equipment in certain panelboards, and see 430.95 for service equipment in motor control centers.
230.72 Grouping of Disconnects.(A) General. The two to six disconnects as permitted in 230.71 shall be grouped. Each disconnect shall be marked to indicate the load served.
Exception: One of the two to six service disconnecting means permitted in 230.71, where used only for a water pump also intended to provide fire protection, shall be permitted to be located remote from the other disconnecting means.
(B) Additional Service Disconnecting Means. The one or more additional service disconnecting means for fire pumps, emergency systems, legally required standby, or optional standby services permitted by 230.2 shall be installed remote from the one to six service disconnecting means for normal service to minimize the possibility of simultaneous interruption of supply.
© Access to Occupants. In a multiple-occupancy building, each occupant shall have access to the occupant’s service disconnecting means.
Exception: In a multiple-occupancy building where electric service and electrical maintenance are provided by the building management and where these are under continuous building management supervision, the service disconnecting means supplying more than one occupancy shall be permitted to be accessible to authorized management personnel only.
What if each townhouse was on its own lot such as our zoning requires. BTW we are under the NEC for electrical, enforced by the state.jar546 said:The IRC would apply for townhouses of course and I am reading the same thing you are. Grouping of disconnects is not required. Plain and simple.If you built townhouses under the NEC, I believe that grouped disconnects are required.
jar546 said:How about looking at the NEC first:
Jar Article 225 does not apply to services. Article 225 is Titled "Outside Branch circuits and feeders".jar546 said:The IRC would apply for townhouses of course and I am reading the same thing you are. Grouping of disconnects is not required. Plain and simple.If you built townhouses under the NEC, I believe that grouped disconnects are required.
chris kennedy said:I removed the 225 reference at the OP request.
You are correct about 230. I know that and looked it up then opened up the electronic version and did a search to be quick and never looked at it again, just assumed I was in the right place. Not the first time that has happened to me.raider1 said:Jar Article 225 does not apply to services. Article 225 is Titled "Outside Branch circuits and feeders".Article 230 regulates electrical services.
If each unit is a separate building then there is no need to group the service disconnecting means.
Chris
Let's not concentrate, just had a 12 hour day, let's relax.jar546 said:Let's get away from how the wires are run and concentrate on the issue of grouping disconnects.
I see your IRC reference above, but I believe the key here is to look at the NEC definition of "Service". In your example the discos would have to be grouped.How about this example:A single group of 4 townhouses.
2 separate services, a 2 gang on the right and a 2 gang on the left.
All service runs from the 2 gang meters are underground and enter the townhouses individually.
Each unit has its own main panel in the basement.
Would your opinion differ if you were under the NEC vs the IRC?
Lets get this party started. Discuss!!
Don't worry about it, slowing down will come naturally with age.jar546 said:I am still PO'd at myself for looking up the right NEC section in the book then bringing up the wrong one on the computer. Not the first time I have done this which is why I think I need to slow down a little.
Done, you owe me a dollar.jar546 said:I am home now so I have to wait until tomorrow to fix my post. Any moderators out there with NEC online want to fix my references?
chris kennedy said:(Guess Hell froze over:evil![]()
Depends on the utility company or the jurisdiction, if they don't require a disconnect at the service the disconnects can be at each unit panel. I'm not sure putting a service on someone else's property is ok. I'd split everything to match the unitsjar546 said:So what is the consensus?If there is a 4 unit townhouse and they install a 2 gang meter on the left side and a 2 gang meter on the right side, do each of the 2 gang services have to have grouped disconnects?