I am talking NEC. Grouping of disconnects has nothing to do with the POCO in our area. Strictly an NEC for this question.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
jar546 said:So what is the consensus?If there is a 4 unit townhouse and they install a 2 gang meter on the left side and a 2 gang meter on the right side, do each of the 2 gang services have to have grouped disconnects?
230.71 deals with the maximum number of disconnects for a single service.jar546 said:There are 2 service drops for 4 units. Read 230.71 please
I have flip flopped on this subject more than once. I have called the NFPA and was told they need to be grouped. That of course is one person's opinion. I have contacted the ICC and nothing was resolved.raider1 said:230.71 deals with the maximum number of disconnects for a single service.4 townhomes would be 4 separate building and each could have a separate service.
So, short NEC answer the 2 2gang meter/disconnect packs would not need to be grouped.
Chris
I agree but it is not a code issue.TJacobs said:Townhouses are separate buildings so they should have separate services, not located on neighboring townhouses.
The location of the disconnect is what determines the premises ("building" is not the correct term since the premises wiring is not limited to the building itself).TJacobs said:Townhouses are separate buildings so they should have separate services, not located on neighboring townhouses.
I'd argue that a disconnect located on someone else's property was not available for the tenant (or could become unavailable easily)brudgers said:The location of the disconnect is what determines the premises ("building" is not the correct term since the premises wiring is not limited to the building itself).If the disconnect is on the end of a structure containing four townhouses, then the premises wiring begins at that point. The wires between the disconnecting means and the building just happen to be exterior.
Some jurisdictions require townhouses to have clustered disconnects to facilitate fire-fighting operations.