Proposed guard shack at a parking lot for tractor trailers. The guard shack is the only building on the site. Its floor area is less than 300 sf.
I am being told by the GC that it will be 7" above grade and therefore the entire guard shack is exempt from accessibility requirements per 1103.2.2.
1103.2.2 Employee work areas. Spaces and elements within employee work area shall only be required to comply with Sections 907.5.2.3.1, 1009 and 1104.3.1 and shall be designed and constructed so that individuals with disabilities can approach, enter and exit the work area. Work areas , or portions of work areas, other than raised courtroom stations in accordance with Section 1108.4.1.4, that are less than 300 square feet in area and located 7 inches or more above or below the ground or finished floor where the change in elevation is essential to the function of the space shall be exempt from all requirements.
The definition of "employee work area" specifically states toilet rooms are not an employee work area, which means the toilet room must be accessible.
I have not seen a site plan, but I do not think a guard shack raised 7" above adjacent grade is essential for a tractor trailer storage lot.
Q1. Am I correct stating that even if the work area is exempt, the toilet room must be accessible?
Q2. If the work area is exempt, could the toilet room also be exempt if the shack is not open to anyone other than employees?
Q3. If the toilet room is accessible, would I be correct to state that the building must be accessible and requires and accessible entrance and exit?
Q4. The last sentence of section 1103.2.2 above " . . .shall be exempt from all requirements." What requirements would be exempt? Anything referenced in Section 1103 or the entire Chapter 11?
Q5. Could section 1103.2.6 Raised areas be used to exempt accessibility requirements?
1103.2.6 Raised areas. Raised areas used primarily for purposes of security, life safety or fire safety including, but not limited to, observation galleries, prison guard towers, fire towers or lifeguard stands are not required to comply with this chapter.
I think trying to use section 1103.2.6 is a stretch, but if it can legitimately be used . . .
Thanks for any insight. I do not try to exempt accessibility requirements except janitor closets, electrical and machinery rooms, and pathways to floors or mezzanines less than 3,000 sf, so these sections are new to me.
Proposed guard shack at a parking lot for tractor trailers. The guard shack is the only building on the site. Its floor area is less than 300 sf.
I am being told by the GC that it will be 7" above grade and therefore the entire guard shack is exempt from accessibility requirements per 1103.2.2.
1103.2.2 Employee work areas. Spaces and elements within employee work area shall only be required to comply with Sections 907.5.2.3.1, 1009 and 1104.3.1 and shall be designed and constructed so that individuals with disabilities can approach, enter and exit the work area. Work areas , or portions of work areas, other than raised courtroom stations in accordance with Section 1108.4.1.4, that are less than 300 square feet in area and located 7 inches or more above or below the ground or finished floor where the change in elevation is essential to the function of the space shall be exempt from all requirements.
The definition of "employee work area" specifically states toilet rooms are not an employee work area, which means the toilet room must be accessible.
I have not seen a site plan, but I do not think a guard shack raised 7" above adjacent grade is essential for a tractor trailer storage lot.
Q1. Am I correct stating that even if the work area is exempt, the toilet room must be accessible?
Q2. If the work area is exempt, could the toilet room also be exempt if the shack is not open to anyone other than employees?
Q3. If the toilet room is accessible, would I be correct to state that the building must be accessible and requires and accessible entrance and exit?
Q4. The last sentence of section 1103.2.2 above " . . .shall be exempt from all requirements." What requirements would be exempt? Anything referenced in Section 1103 or the entire Chapter 11?
Q5. Could section 1103.2.6 Raised areas be used to exempt accessibility requirements?
1103.2.6 Raised areas. Raised areas used primarily for purposes of security, life safety or fire safety including, but not limited to, observation galleries, prison guard towers, fire towers or lifeguard stands are not required to comply with this chapter.
I think trying to use section 1103.2.6 is a stretch, but if it can legitimately be used . . .
Thanks for any insight. I do not try to exempt accessibility requirements except janitor closets, electrical and machinery rooms, and pathways to floors or mezzanines less than 3,000 sf, so these sections are new to me.