The Building Code says 'guards shall comply with...' It does not say 'required guards', so even a non-required guard must comply. As noted earlier, it cannot create a false sense of security.
The IRC takes a slightly different approach. Some sections say 'required guards shall' and other simply say 'guards shall'. Height and opening limitations in the IRC only apply to 'required guards' while the loading requirements apply to all guards per Section R301.5 and Table R301.5.