• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Hallway Width

But considering there is a men's door in the aisle both closer and latch that would mean there has to be 48" minimum hallway width.

You are correct. If there is no latch on the bathroom door then 44" is the minimum required.
If you have a closure and a latch on the exit door then you will be back to 48" again for the minimum width at the exit door and for the 48" in front of the door

1633230129740.png
 
So if the back door is not available as a customer exit, then it becomes a dead end corridor … right?
The back door is required to meet the 2 exit access requirement 1015.1. The customers will not park behind the building because it's a service road. If there is a fire then they can exit the back door if needed. The back door will be unlocked at all times during business hours.
 