Mech
REGISTERED
2009 ICC A117.1
ADA
Are both forward and parallel approaches for hand dryers acceptable?
Must the approach be centered on the hand dryer?
I did not see anything mentioned in either A117.1 or ADA. The only thing I found was a Maximum Reach Depth and Height Table in A117.1 (Chapter 6, Table 603.6). Did I miss the information somewhere?
603.6 Operable Parts. Operable parts on towel dispensers and hand dryers serving accessible lavatories shall comply with Table 603.6.
TABLE 603.6 MAXIMUM REACH DEPTH AND HEIGHT
[TABLE=width: 677]
[TR]
[TD]Maximum
Reach Depth
[/TD]
[TD]0.5 inch(13 mm)[/TD]
[TD]2 inches(51 mm)[/TD]
[TD]5 inches(125 mm)[/TD]
[TD]6 inches(150 mm)[/TD]
[TD]9 inches(230 mm)[/TD]
[TD]11 inches(280 mm)[/TD]
[/TR]
[TR]
[TD]
Maximum
Reach Height
[/TD]
[TD]48 inches(1220 mm)[/TD]
[TD]46 inches(1170 mm)[/TD]
[TD]42 inches(1065 mm)[/TD]
[TD]40 inches(1015 mm)[/TD]
[TD]36 inches(915 mm)[/TD]
[TD]34 inches(865 mm)[/TD]
[/TR]
[/TABLE]
Thanks
ADA
Are both forward and parallel approaches for hand dryers acceptable?
Must the approach be centered on the hand dryer?
I did not see anything mentioned in either A117.1 or ADA. The only thing I found was a Maximum Reach Depth and Height Table in A117.1 (Chapter 6, Table 603.6). Did I miss the information somewhere?
603.6 Operable Parts. Operable parts on towel dispensers and hand dryers serving accessible lavatories shall comply with Table 603.6.
TABLE 603.6 MAXIMUM REACH DEPTH AND HEIGHT
[TABLE=width: 677]
[TR]
[TD]Maximum
Reach Depth
[/TD]
[TD]0.5 inch(13 mm)[/TD]
[TD]2 inches(51 mm)[/TD]
[TD]5 inches(125 mm)[/TD]
[TD]6 inches(150 mm)[/TD]
[TD]9 inches(230 mm)[/TD]
[TD]11 inches(280 mm)[/TD]
[/TR]
[TR]
[TD]
Maximum
Reach Height
[/TD]
[TD]48 inches(1220 mm)[/TD]
[TD]46 inches(1170 mm)[/TD]
[TD]42 inches(1065 mm)[/TD]
[TD]40 inches(1015 mm)[/TD]
[TD]36 inches(915 mm)[/TD]
[TD]34 inches(865 mm)[/TD]
[/TR]
[/TABLE]
Thanks