REGISTERED
ANSI A117.1 - 2003
This is a proposed 2" pipe column (2-3/8" OD) with a 1-1/4" pipe handrail (1-5/8" OD) I have been asked to review. Does this comply or not?
I'm thinking it does not comply since the horizontal projection of the column occurs within 3/8" from the bottom of the handrail. Section 505.6 Gripping Surface, Handrail brackets or balusters attached to the bottom surface of the handrail shall not be considered obstructions, provided they comply with the following criteria --> Exception B - horizontal projections beyond the sides of the handrail occur 1-1/2" minumum below the bottom of the handrail . . .
Thanks in advance.
This is a proposed 2" pipe column (2-3/8" OD) with a 1-1/4" pipe handrail (1-5/8" OD) I have been asked to review. Does this comply or not?
I'm thinking it does not comply since the horizontal projection of the column occurs within 3/8" from the bottom of the handrail. Section 505.6 Gripping Surface, Handrail brackets or balusters attached to the bottom surface of the handrail shall not be considered obstructions, provided they comply with the following criteria --> Exception B - horizontal projections beyond the sides of the handrail occur 1-1/2" minumum below the bottom of the handrail . . .