Energystar
SAWHORSE
I am building a home with a heated garage. The garage is insulated well below prescriptive code requirements and of course the garage door cannot meet fenestration requirements. However, the customer wants to install a PTAC unit in the garage to make it more comfortable, but not to the temperatures required for conditioned space. The plan reviewer says that the installation of the PTAC would violate the following section of the code because it would be considered “conditioned space”.

The IRC defines conditioned space as follows:

I would argue that the garage is certainly not within the “building thermal envelope” and is therefore not “conditioned space”.

As you can see, the two definitions rely on each other. I’m pretty sure I got scolded for that in English class at one time or another.
Another strange issue is that as written N1102.1 only applies to homes using the Prescriptive Compliance Option. Even though I am using the Performance Compliance Option, the official still insists it is in violation.
I find it hard to believe that this is the intent of the code.

The IRC defines conditioned space as follows:

I would argue that the garage is certainly not within the “building thermal envelope” and is therefore not “conditioned space”.

As you can see, the two definitions rely on each other. I’m pretty sure I got scolded for that in English class at one time or another.
Another strange issue is that as written N1102.1 only applies to homes using the Prescriptive Compliance Option. Even though I am using the Performance Compliance Option, the official still insists it is in violation.
I find it hard to believe that this is the intent of the code.