Help with Live Load Span

Francis Vineyard

REGISTERED
Joined
Jan 1, 2010
Messages
3,105
Location
Charlottesville, VA
In accordance with Section R301.7 why doesn't the floor joist span tables use L/240 as permitted in the referenced tables and (2015) R502.5(3)?

R301.7 Deflection. The allowable deflection of any structural member under the live load listed in Sections R301.5 and R301.6 or wind loads determined by Section R301.2.1 shall not exceed the values in Table R301.7.
upload_2016-9-29_7-56-21.png

upload_2016-9-29_7-57-4.png

upload_2016-9-29_7-58-24.png
upload_2016-9-29_7-59-33.png
 
I am not familiar with the IRC. For floor members in the IBC, the live load deflection limit is L/360 and the live+dead load deflection limit is L/240. Maybe some of the deflection in the IRC is similar.
 
Phil, could we assume the header span has a deflection of L/240 for exterior walls for floors with a dead load of 20 psf. and not 10 psf?

Is this logical for decks and open porches too?
 