Hold down{PIC}
Is this what the engineer had in mind?
Builder Bob said:
Need to really look at the structural plans..... Don't think a sane Engineer would ever specify two HD's on the same post/column/corner.
That's funny. I once saw an engineer specify #9 @ 1" O.C. for the bearing plate of a precast beam.
I was the superintendent on the RiverPointe building in Bend in the mid 80's. The structural plans called for two identical hold downs on a dozen six by six corner studs. That's how I did it. Everybody seemed happy with it.
Course, times were simpler then.
Bill
What about Section R403.1.6, from the `06 IRC?
"R403.1.6 Foundation anchorage.....When braced wall panels are supported directly
on continuous foundations, the wall wood sill plate or cold-formed steel bottom track
shall be anchored to the foundation in accordance with this section.
The wood sole plate at exterior walls on monolithic slabs and wood sill plate shall be
anchored to the foundation with anchor bolts spaced a maximum of 6 feet (1829 mm) on
center............There shall be a minimum of two bolts per plate section with one bolt located
not more than 12 inches (305 mm) or less than seven bolt diameters from each end
of the plate section........In Seismic Design Categories D0, D1 and D2, anchor bolts shall
be spaced at 6 feet (1829mm) on center and located within 12 inches (305 mm) of the
ends of each plate section at interior braced wall lines when required by Section
R602. 10.9 to be supported on a continuous foundation.........Bolts shall be at least ½ inch
(13 mm) in diameter and shall extend a minimum of 7 inches (178 mm) into masonry or
concrete..........Interior bearing wall sole plates on monolithic slab foundation shall be
positively anchored with approved fasteners.........A nut and washer shall be tightened on
each bolt of the plate........Sills and sole plates shall be protected against decay and
termites where required by Sections R3 19 and R320..........Cold-formed steel framing
systems shall be fastened to the wood sill plates or anchored directly to the foundation
as required in Section R505.3.1 or R603.1.1.
Exceptions:1.........Foundation anchorage, spaced as required to provide equivalent anchorage to
½-inch-diameter (13 mm) anchor bolts.
2........Walls 24 inches (610 mm) total length or shorter connecting offset braced wall
panels shall be anchored to the foundation with a minimum of one anchor bolt located
in the center third of the plate section and shall be attached to adjacent braced wall
panels per Figure R602. 10.5 at corners.
3.........Walls 12 inches (305 mm) total length or shorter connecting offset braced wall
panels shall be permitted to be connected to the foundation without anchor bolts......The
wall shall be attached to adjacent braced wall panels per Figure R602.10.5 at corners.
Me thinks that the inside "hold down" is too close to the sill plate end.
[/color]$ $ $ $[/font][/size]
If it was a hold down designed to hold down that wall/sole plate it would be too close. But if you follow the orange string down to the sole plate you will see the anchor bolt for that wall. It's almost completely hidden by the stud.
Bill
I think the 4 bright bolts split the 4x corner stud, so the 4 dark bolts are there only to hold the two halves together at each bright bolt location. See the split above the strap?
nah, look at the bottom across from the the "dark" bolts, there is a hold down there. If the engineer buys off on it, move on unless your can prove them wrong.