TheCommish
SAWHORSE
yes we have been do this path before while discussing pull down stair in a garage ceilings. Given 2015 IRC, section 302.5 and table 302.6, the holes are hockey puck LED (replacement for full recessed cans)
R302.5.2 Duct penetration. Ducts in the garage and ducts
penetrating the walls or ceilings separating the dwelling
from the garage shall be constructed of a minimum No. 26
gage (0.48 mm) sheet steel or other approved material and
shall not have openings into the garage.
R302.5.3 Other penetrations. Penetrations through the
separation required in Section R302.6 shall be protected as
required by Section R302.11, Item 4.
They are not ducts or pipes so other penetrations see 302.11 item 4, 302.11 is fireblockeig
4. At openings around vents, pipes, ducts, cables and
wires at ceiling and floor level, with an approved material
to resist the free passage of flame and products of
combustion. The material filling this annular space
shall not be required to meet the ASTM E 136 requirements.
LED is not a vent, pipe, duct, cable and wire.
let the discourse begin
R302.5.2 Duct penetration. Ducts in the garage and ducts
penetrating the walls or ceilings separating the dwelling
from the garage shall be constructed of a minimum No. 26
gage (0.48 mm) sheet steel or other approved material and
shall not have openings into the garage.
R302.5.3 Other penetrations. Penetrations through the
separation required in Section R302.6 shall be protected as
required by Section R302.11, Item 4.
They are not ducts or pipes so other penetrations see 302.11 item 4, 302.11 is fireblockeig
4. At openings around vents, pipes, ducts, cables and
wires at ceiling and floor level, with an approved material
to resist the free passage of flame and products of
combustion. The material filling this annular space
shall not be required to meet the ASTM E 136 requirements.
LED is not a vent, pipe, duct, cable and wire.
let the discourse begin