• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Home Made Fuses for a Temporary Service

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,057
Location
Somewhere Too Hot & Humid
Does anyone know the rating on these fuses?
attachment.php


View attachment 2147

View attachment 2147

/monthly_2015_05/IMAG0089.jpg.ec13d582827cab203c515ba3a1345e42.jpg
 
for #6 CU: about 1200A for 2 seconds to arc plasma flash and molten metal spatter. Most power company transformers can deliver 35 to 50,000A on full fault failure.
 
Well it is after all a temporary power. Bare #6 in free air should handle 80 amps. #8 should go 60 amps no sweat.
 