Hi all,
Running into some code interpretation challenges and would appreciate your input.
Project Overview:
Per CBC/CFC 1009.2.1, standby power for the elevator is required unless a 2-hour horizontal exit is provided on every floor (excluding the exit discharge level), assuming full sprinklers.
Since the roof is occupied but can’t feasibly include a horizontal exit, does this disqualify the exemption entirely? Or can the exemption still apply to the floors below, thereby avoiding the need for standby power?
I’ve attached a PDF of the plans. Would love any suggestions on whether a horizontal exit can be added with minimal project impact—or if standby power is ultimately unavoidable here.
Thanks in advance for your help!
Running into some code interpretation challenges and would appreciate your input.
Project Overview:
- 5-story, 19-unit apartment building
- 4 levels of R-2 above 1 level of enclosed carport (U)
- Fully sprinklered (NFPA 13)
- Occupied rooftop terrace
- 2022 California Building Code
Per CBC/CFC 1009.2.1, standby power for the elevator is required unless a 2-hour horizontal exit is provided on every floor (excluding the exit discharge level), assuming full sprinklers.
Since the roof is occupied but can’t feasibly include a horizontal exit, does this disqualify the exemption entirely? Or can the exemption still apply to the floors below, thereby avoiding the need for standby power?
I’ve attached a PDF of the plans. Would love any suggestions on whether a horizontal exit can be added with minimal project impact—or if standby power is ultimately unavoidable here.
Thanks in advance for your help!