I've run into this issue twice in the last 2 weeks so it must be a new trend. One hotel is under construction with door frames installed, and the other is in the design stage. The bathroom door within the guest room is a pair of 1'-5" or 1'-6" wide doors (each leaf). IMO, the IBC requires at least one leaf of a pair to provide 32" clear, and there isn't a relevant exception. The accessibility standards also require one leaf to provide 32" clear, but this would apply to accessible units and the egress would apply to all units. We've already talked about whether a bathroom door has to meet egress requirements and I think most of us agreed that it would. Is this design code-compliant? What am I missing?
View attachment 1755
Here's the section from the 2009 IBC:1008.1.1 Size of doors. The minimum width of each door opening shall be sufficient for the occupant load thereof and shall provide a clear width of 32 inches (813 mm). Clear openings of doorways with swinging doors shall be measured between the face of the door and the stop, with the door open 90 degrees (1.57 rad). Where this section requires a minimum clear width of 32 inches (813 mm) and a door opening includes two door leaves without a mullion, one leaf shall provide a clear opening width of 32 inches (813 mm). The maximum width of a swinging door leaf shall be 48 inches (1219 mm) nominal. Means of egress doors in a Group I-2 occupancy used for the movement of beds shall provide a clear width not less than 41 1/2 inches (1054 mm). The height of door openings shall not be less than 80 inches (2032 mm). Exceptions:1. The minimum and maximum width shall not apply to door openings that are not part of the required means of egress in Group R-2 and R-3 occupancies.2. Door openings to resident sleeping units in Group I-3 occupancies shall have a clear width of not less than 28 inches (711 mm).3. Door openings to storage closets less than 10 square feet (0.93m2) in area shall not be limited by the minimum width.4. Width of door leaves in revolving doors that comply with Section 1008.1.4.1 shall not be limited.5. Door openings within a dwelling unit or sleeping unit shall not be less than 78 inches (1981 mm) in height.6. Exterior door openings in dwelling units and sleeping units, other than the required exit door, shall not be less than 76 inches (1930 mm) in height.7. In other than Group R-1 occupancies, the minimum widths shall not apply to interior egress doors within a dwelling unit or sleeping unit that is not required to be an Accessible unit, Type A unit or Type B unit.View attachment 1755
/monthly_2013_01/572953e813f2e_HotelBathroomPair.JPG.7e990d0d69443d0c115fd11ac3511356.JPG
View attachment 1755
Here's the section from the 2009 IBC:1008.1.1 Size of doors. The minimum width of each door opening shall be sufficient for the occupant load thereof and shall provide a clear width of 32 inches (813 mm). Clear openings of doorways with swinging doors shall be measured between the face of the door and the stop, with the door open 90 degrees (1.57 rad). Where this section requires a minimum clear width of 32 inches (813 mm) and a door opening includes two door leaves without a mullion, one leaf shall provide a clear opening width of 32 inches (813 mm). The maximum width of a swinging door leaf shall be 48 inches (1219 mm) nominal. Means of egress doors in a Group I-2 occupancy used for the movement of beds shall provide a clear width not less than 41 1/2 inches (1054 mm). The height of door openings shall not be less than 80 inches (2032 mm). Exceptions:1. The minimum and maximum width shall not apply to door openings that are not part of the required means of egress in Group R-2 and R-3 occupancies.2. Door openings to resident sleeping units in Group I-3 occupancies shall have a clear width of not less than 28 inches (711 mm).3. Door openings to storage closets less than 10 square feet (0.93m2) in area shall not be limited by the minimum width.4. Width of door leaves in revolving doors that comply with Section 1008.1.4.1 shall not be limited.5. Door openings within a dwelling unit or sleeping unit shall not be less than 78 inches (1981 mm) in height.6. Exterior door openings in dwelling units and sleeping units, other than the required exit door, shall not be less than 76 inches (1930 mm) in height.7. In other than Group R-1 occupancies, the minimum widths shall not apply to interior egress doors within a dwelling unit or sleeping unit that is not required to be an Accessible unit, Type A unit or Type B unit.View attachment 1755
/monthly_2013_01/572953e813f2e_HotelBathroomPair.JPG.7e990d0d69443d0c115fd11ac3511356.JPG