• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

How do you ensure that the rebar in the footer gets bonded?

Where there is a membrane under all of the foundation concrete such that the concrete is not in direct contact with the soil a ufer ground is not appropriate.
 
We verify the UFER at footing inspection. Commercial we document the location and require it by the service main or where called for on plans. Residential we require it in the garage and document its location on the footing inspection.
 
Inspected at the footing steel inspection. I like the green spray paint idea.

Any body have a preference where the connection to the building steel should be made and are you making them scratch the paint off at the connection?