How do you fix this?

You cant....

Why does it appear the neither the shower nor the penetration behind it are protected (firestopped)? The one behind the shower looks to be original given the lack of any spalling at the corner.
 
Note the piece of rebar extending through the opening. Unless somebody can show that the rebar is not needed the repair needs to provide concrete, or the equivalent, of a certain thickness around the reinforcement. This might mean that the shower pan needs to be located higher.

Plumbers have a reputation of providing undesirable holes in structural members.
 
@ ~ @

If the intent of the condition in the picture is to
replace the concrete, I am not sure that the "concrete
fix" would have the same structural strength as the
existing floor.

If someone were to ask me what I would do, I would
draw a larger sized square around the opening, and
like the existing pipe hangar, I would drill in some
stainless steel, high strength bolts and attach a
galvanized metal frame \ box to the concrete........Next,
I would seal completely the metal framing, either:

(1) by welding everything together, or (2) by bolting
everything together..........Next, I would apply a thick
layer of fire rated caulking to everything and let setup.



** Rembo **, ...do you know what the engineer actually
did ?


@ ~ @
 
@ ~ @

If the intent of the condition in the picture is to
replace the concrete, I am not sure that the "concrete
fix" would have the same structural strength as the
existing floor.


@ ~ @

Some of the Ardex and Hilti concrete repair products are used to repair bridges, I don't think whats shown in the OP's image will be a problem.
 
Note the piece of rebar extending through the opening. Unless somebody can show that the rebar is not needed the repair needs to provide concrete, or the equivalent, of a certain thickness around the reinforcement. This might mean that the shower pan needs to be located higher.

Plumbers have a reputation of providing undesirable holes in structural members.