How do you see this
tbz said:
Steveray,Ok just to make myself even more confused. Does the IBC even cover pathways within a parking lot or is that left to A117.1 and ADAAG?
Yes it is covered under the IBC
1101.1 Scope.
The provisions of this chapter shall control the design and construction of facilities for accessibility to physically disabled persons.
1101.2 Design.
Buildings and facilities shall be designed and constructed to be accessible in accordance with this code and ICC A117.1.
FACILITY. All or any portion of buildings, structures, site improvements, elements and pedestrian or vehicular routes located on a site.
ICE said:
The roof looks like it needs help.
They all look that way around here.....
Tom...yes I would have jurisdiction over what you show...Use "accessible parking"...it's nicer...
Exemptions from permit....
6. Sidewalks and driveways not more than 30 inches (762 mm) above adjacent grade, and not over any basement or story below and are not part of an accessible route.
And this is why I was asking about the site or public way and other details that make it an issue or not....
SECTION 1104 ACCESSIBLE ROUTE
1104.1 Site arrival points. Accessible routes within the site shall be provided from public transportation stops; accessible parking; accessible passenger loading zones; and public streets or sidewalks to the accessible building entrance served.
Exception: Other than in buildings or facilities containing or serving Type B units, an accessible route shall not be required between site arrival points and the building or facility entrance if the only means of access between them is a vehicular way not providing for pedestrian access.
1104.2 Within a site. At least one accessible route shall connect accessible buildings, accessible facilities, accessible elements and accessible spaces ******** that are on the same site.*****
Exception: An accessible route is not required between accessible buildings, accessible facilities, accessible elements and accessible spaces that have, as the only means of access between them, a vehicular way not providing for pedestrian access.
The exceptions do not REQUIRE the accessible route to be installed. However when an accessible route is provided it has to comply with the code requirements.