• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

How do you use 5occ/sqft in a night club? IBC 1004.5.1

Brian 2

Registered User
Joined
May 18, 2017
Messages
17
Location
Denver
When using the 5occ/sqft standing space occupant load for a night club, is it permissible to use that factor in the entire space? For example, there is just one large open room used entirely as a night club (yes there maybe a stage / bar too but for discussion only considering net floor area of the rest of the room). The confusion lies in 2018 IBC 1004.5.1 where it states the occupant load of a space should not exceed 7 occupants per sqft; the commentary goes further to say that the intent of the 5occ/sqft is only intended for a smaller gathering space in a larger room such as a bar where the rest of the room would be 15occ/sqft. So do you load a night club at 5 or 7 occupant / sqft? Does IBC 1004.5.1 intent to limit the max occupant load of any room to not more than 7 occ/sqft; even though it is titled “increased occupant load”?
 
Section 1004.5.1 may be used when you increase the occupant load from a load factor provided in Table 1004.5. Thus a classroom's occupant load (20 sq. ft. per occupant) can be increased to a maximum of 7 sq. ft. per occupant.

Thus, the standing space and concentrated assembly occupant load factors (5 and 7 sq. ft. per occupant, respectively) cannot be increased.

I would apply the standing space occupant load factor to dance floor areas and areas where no tables and chairs are provided.
 
Top