How Many Violations Can You Spot? (Monitor Installation)
Alias
State of Disbelief
Okay, for those that have looked at the unpermitted monitor installation thread, here are a few pictures of the install.Sue, shaking my head.....oy vey! :roll:
/monthly_2010_05/572953dae3de0_pictures016.jpg.60ffba41a00e854bb8855ee8711b8116.jpg
/monthly_2010_05/572953dae7ea7_pictures019.jpg.da0562f16c934536280b1ec34eb93ae7.jpg
/monthly_2010_05/572953daebe04_pictures012.jpg.3c2440994a35a80c09028f14ee554a21.jpg
Re: How Many Violations Can You Spot? (Monitor Installation)
sue,
the tank needs to be seismically anchored to a pt post cemented into the ground or other method, we require an incidental spill pan that would contain small leaks from filling operations,changing filters etc.,need bollards for tank protection,don't see a fuel guage on top,would need to see oil line connection to tank for filter and valve set-up,check stove inside for fusible link valve. there are a few issues to begin with.wish i was there! not :mrgreen:
My answers -
Fuel oil piping: per manufacturer rep, not sold in CA. If I allow the piping, it needs to be sleeved for this type of installation and attached to the building with appropriate hangers.
Joint/connection is not protected from the concrete (lime) loading dock hence allowing corrosion of the copper piping and fittings. These also need to have a plastic 'shrink wrap' applied to protect it from the elements. It should also be moved away from the loading dock due to the fact that it is a loading dock and though not in use currently it could be at a later date.
Tank not set evenly. It actually lists a bit towards the parking lot. Bollards to protect the tank from vehicles in the adjacent parking lot.
Sue, where the west still lives.......... :roll: :mrgreen:
pwood said:
sue, the tank needs to be seismically anchored to a pt post cemented into the ground or other method, we require an incidental spill pan that would contain small leaks from filling operations,changing filters etc.,need bollards for tank protection,don't see a fuel guage on top,would need to see oil line connection to tank for filter and valve set-up,check stove inside for fusible link valve. there are a few issues to begin with.wish i was there! not :mrgreen:
Thanks for the input pwood! I pm'ed you with some further questions.
Sue, where the west still lives...........
Re: How Many Violations Can You Spot? (Monitor Installation)Actual monitor installation. The stand is 2x4 with a plywood top. It is anchored into the block wall. The monitor is about 3 feet off the floor and the only fasteners attaching the monitor to the stand are a couple of small screws through the bottom metal plate. Wonderful, eh?Now when we discussed this, I informed the installer that the monitor heater needed to be strapped to the wall for seismic stability.Sue :x
/monthly_2010_05/572953b43b6f7_pictures021.jpg.ce7126c218d1caccf92019c1c85f1c52.jpg
/monthly_2010_05/572953b43fc11_pictures022.jpg.1f0067b11b99a372a221d4064c17d854.jpg
/monthly_2010_05/572953b4edb5a_pictures023.jpg.cbe4c1198c7127e9e762b52c9e54c377.jpg
All you need is Gomer Pyle to go with the quonset hut, then it makes sense.
Come on Sue........they have their water supply hydrant on site :lol:
Clearance to combustibles issue with the items next to it also :D
FM William Burns said:
Come on Sue........they have their water supply hydrant on site :lol:Clearance to combustibles issue with the items next to it also :D
Hehehe.......yep, lots of four legged volunteers. :)
I talked to the shop owner about the location of the doggie sweaters, I'll check to make sure they are moved next time I drop by the shop.
Sue