Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
It's always nice to know why the DW drain connection is not correct:
2015 IRC
P2717.2 Sink and dishwasher.
The combined discharge from a dishwasher and a one- or two-compartment sink, with or without a food-waste disposer, shall be served by a trap of not less than 1-1/2 inches (38 mm) in outside diameter. The dishwasher discharge pipe or tubing shall rise to the underside of the counter and be fastened or otherwise held in that position before connecting to the head of the food-waste disposer or to a wye fitting in the sink tailpiece.
High loop island vent with the dishwasher discharging to the fixture trap.Now the next learning question is what do you do when the DW is in island that doesn't have a sink? (and the OPs photo may be just that situation.
Thank you for posting that. This is the information I was hoping to get posted as it provides definitive answers to relevant subjects when people search.
I disagree... any company can put a product out to market and have instructions on how to install. That does not mean that it complies with the code or is allowable under the code.manufacturers installation instructions overrides the code section.
I disagree... any company can put a product out to market and have instructions on how to install. That does not mean that it complies with the code or is allowable under the code.
What the code does allow for, is for manufacturers who have their products tested and listed by an approved agency, to follow the listing developed during testing. It is not a complete free for all.
IMC SECTION 304
INSTALLATION
304.1 General. Equipment and appliances shall be installed
as required by the terms of their approval, in accordance with
the conditions of the listing, the manufacturer’s installation
instructions and this code. Manufacturer’s installation
instructions shall be available on the job site at the time of
inspection.
IMC SECTION 304
INSTALLATION
304.1 General. Equipment and appliances shall be installed
as required by the terms of their approval, in accordance with
the conditions of the listing, the manufacturer’s installation
instructions and this code. Manufacturer’s installation
instructions shall be available on the job site at the time of
inspection.
304.2 Conflicts. Where conflicts between this code and the
conditions of listing or the manufacturer’s installation
instructions occur, the provisions of this code shall apply.
Exception: Where a code provision is less restrictive than
the conditions of the listing of the equipment or appliance
or the manufacturer’s installation instructions, the conditions
of the listing and the manufacturer’s installation
instructions shall apply.
manufacturers installation instructions overrides the code section.
No one is suggesting your OP picture would pass any code or manufactures installation instructionIn addition, you will not find mfg installation instructions that will allow this type of installation. Show me one.
Is your BO willing to accept something other than a listing?
No one is suggesting your OP picture would pass any code or manufactures installation instruction
We just got off on another rabbit trail
Who qualifies the "Listing" lab or firm?
105.3.2 Testing Agency
Tests shall be performed by an approved agency.
Disagree. The more restrictive applies.
Oh joy ... now we’re going to beat a dead rabbit, like the discussion about dead-end corridors.We just got off on another rabbit trail
It's always nice to know why the DW drain connection is not correct:
2015 IRC
P2717.2 Sink and dishwasher.
The combined discharge from a dishwasher and a one- or two-compartment sink, with or without a food-waste disposer, shall be served by a trap of not less than 1-1/2 inches (38 mm) in outside diameter. The dishwasher discharge pipe or tubing shall rise to the underside of the counter and be fastened or otherwise held in that position before connecting to the head of the food-waste disposer or to a wye fitting in the sink tailpiece.